Thankd God, Steven was’nr injured that much. Im sure, he can still perform in the future, its his life. Ok, people looking out for the fallout of the Steven Tyler fall incident, we got the skinny. After the Steven Tyler fall incident during an Aerosmith concert at the Sturgis Motorcycle Rally in South Dakota, he was airlifted to a hospital, and treated for injuries to his head and shoulders. He did not suffer a concussion, had a couple of broken bones and a few stitches. He broke his shoulder so all concert dates will be postponed for up to two months. A broken shoulder is a painful injury, especially when the singer is over 60 years of age. Ticket holders need not fret over the Steven Tyler fall – dates are merely postponed, so you won’t need a cash loan for new tickets.
From what I see I question what happened. Did the (fuse)fault happen at the primary or secondary side of the transformer? I would never let a show go to sound check with the shape of the service to beginn with. Fro the two pictures above I see:
Multiple conductors under a single lug.
Missing grounded conductor (Neutral)buss
Aluminum conductors impropoerly installed (torgee,oxide inhibitor, multilugged, size, etc…)
200 amp service would require 4/0 aluminum conductors)
Missing ground bar, gounding and bonding.
Missing bonding screw ( Needs to be green)
Missing bonding bushings
Open knockouts
Missing labels
One more thing… I like the tape to hold the cover closed….
...Oops! Sorry for the spelling, I forgot spell check!
Come on you guys. you know that this is not there first concert for this hall so this has been going on for years. With some of the biggest sound and lighting companies running off this box.When we come to this neck of the woods we will ask for a generator.in the past we have rewired the service feed before the show went on @ $300.00 a hour that pays my electrician for the day we get all money up front.
Thanks for taking the time to discuss and share this with us, I for one feel strongly about it and really enjoyed learning more about this topic. I can see that you possess a degree of expertise on this subject, I would very a lot like to hear much more from you on this matter
JN0-660
HP2-Z16
70-685
642-642
642-457
HP2-E38
000-106
70-648
We get with the house electrician tie in. meter the load.then we lock it down. if we can not lock it,
we check during sound check,before and during the show
that way you will not be writing about it later.